Correct. And that is exactly how my Generac is wired. I identified each circuit's neutral, disconnected from the main panel bar, and then wire nutted to a neutral line from the Generac neutral bar. This is how I discovered a couple of circuits that shared and a neutral line thus causing my dilemma with the fridge.
I did do a little more testing and found that my PowerBoost will ground fault when switching both ways (Utility to Generator) and (Generator to Utility). But since there was zero faults after post switch over to Gen, I'm happy.
I did do a little more testing and found that my PowerBoost will ground fault when switching both ways (Utility to Generator) and (Generator to Utility). But since there was zero faults after post switch over to Gen, I'm happy.
#22
So is this essentially taking the bonded connection in the main circuit panel and making it floating to get around the ground fault issue with the powerboost? Reason I ask is I installed a pro tran on our panel not knowing of the powerboost issue and it having a bonded neutral just like the house panel (newer construction). Now I feel stuck and am trying to find a workaround that won't kill me like unhooking the ground.
#23
There isn’t a work around that is safe and to National Electrical Code
#24
I hate to revive such an old thread, but can one of you electricians give me a little guidance as to how to help the electrician that I've hired. He has removed a group of breakers that I want the truck to power from the main panel and put them in a sub-panel controlled by a Generac Transfer Switch. Everything works fine if the ground is disconnected, when he connects the ground, it trips the truck. At this point of the the install, what needs to be done to resolve this issue?
#25
Senior Member
I hate to revive such an old thread, but can one of you electricians give me a little guidance as to how to help the electrician that I've hired. He has removed a group of breakers that I want the truck to power from the main panel and put them in a sub-panel controlled by a Generac Transfer Switch. Everything works fine if the ground is disconnected, when he connects the ground, it trips the truck. At this point of the the install, what needs to be done to resolve this issue?
The following users liked this post:
Hullguy (01-22-2024)
#26
#27
Senior Member
I'm assuming this entire panel is fed from ProPower, how do you energize it? I ask because that doesn't look like the Generac neutral switching panels, or any of the other bonded generator panels I've seen mentioned in the past. Are you putting the truck neutral in to the panel when it's hooked up or leaving whatever is in place there? Is there a neutral/ground bond in the panel? I don't see one, but it's difficult to tell on my phone.
#28
I'm assuming this entire panel is fed from ProPower, how do you energize it? I ask because that doesn't look like the Generac neutral switching panels, or any of the other bonded generator panels I've seen mentioned in the past. Are you putting the truck neutral in to the panel when it's hooked up or leaving whatever is in place there? Is there a neutral/ground bond in the panel? I don't see one, but it's difficult to tell on my phone.
Everything works fine if the ground is disconnected on either end of the cable coming from the plug in the garage to the Generac. Obviously, the code inspector didn't like that idea, lol.
connected via plug in the garage.
#29
Senior Member
Ok, I think I see the issue, but again, the pictures are hard to view on my phone. The transfer switch is only swapping the two hot legs, all the neutrals are connected together. There's probably a neutral-ground bond in one of the panels causing your issue. I'm not sure if there will be a way to make it work without a different transfer switch, but the electrician can hopefully help you out.
The following users liked this post:
Donas (01-22-2024)
#30
Ok, I think I see the issue, but again, the pictures are hard to view on my phone. The transfer switch is only swapping the two hot legs, all the neutrals are connected together. There's probably a neutral-ground bond in one of the panels causing your issue. I'm not sure if there will be a way to make it work without a different transfer switch, but the electrician can hopefully help you out.