7.2 Propower issue

Thread Tools
 
Search this Thread
 
Old Sep 6, 2025 | 03:40 PM
  #1  
Lizardking's Avatar
Thread Starter
Senior Member
15 Year Member
Photogenic
Photoriffic
 
Joined: Sep 2008
Posts: 218
Likes: 107
Default 7.2 Propower issue

My truck is a 2023 PowerBoost with the 7.2kw propower option.
My first attempt to use the propower.
I had to haul my 20gal air compressor to an RV storage facility to air up the tires on my Class A motorhome. The compressor pulls 13amps. At home I have it plugged into the normal 15amp outlet in the garage.
I plugged the compressor into the A side of the bed, then the B side. In both cases the truck told me my device was pulling too much power.
I plugged the compressor into the dash outlet, and it worked fine.
Is there an issue?
Reply
Old Sep 6, 2025 | 06:50 PM
  #2  
Bluegrass's Avatar
Senior Member
5 Year Member
Community Builder
Community Influencer
Top Answer: 1
 
Joined: Mar 2021
Posts: 4,798
Likes: 2,396
Default

Question;
Does the Compressor have a ground pin on its Plug?
The outlets are supposed to offer 20 amps each at 120 volts AC.
Good luck.
Reply
Old Sep 7, 2025 | 06:32 AM
  #3  
Fordstream's Avatar
Senior Member
Liked
Loved
Community Favorite
 
Joined: Feb 2022
Posts: 109
Likes: 51
From: SW Florida
Default

I've had an issue with compressors starting with inverter systems before, but have not tried using a larger compressor off my truck. Maybe try using an dogbone adapter that splits the 30 amp 240 volt twist lock into a couple of 120 v outlets. I've done that for a large table saw and it handled the large inrush current fine and worked as expected.
Reply
Old Sep 7, 2025 | 07:06 AM
  #4  
henfield's Avatar
Senior Member First F150
5 Year Member
Community Influencer
Liked
Loved
 
Joined: Apr 2020
Posts: 4,699
Likes: 1,975
From: Boston, Ma
Default

Good answer. What you are running up against is the surge demand for power v continuous demand for power. The Initial or start up (surge) demand is always higher than the sticker label on the equipment.
Reply
Old Sep 7, 2025 | 10:11 AM
  #5  
Jim Fountain's Avatar
Jim Fountain
5 Year Member
Liked
 
Joined: Jan 2021
Posts: 201
Likes: 94
From: Austin Tx
Default

Originally Posted by Fordstream
I've had an issue with compressors starting with inverter systems before, but have not tried using a larger compressor off my truck. Maybe try using an dogbone adapter that splits the 30 amp 240 volt twist lock into a couple of 120 v outlets. I've done that for a large table saw and it handled the large inrush current fine and worked as expected.
Start up current too high. Dogbone will probably fix it. Try this:

Amazon Amazon
Reply
Old Sep 8, 2025 | 08:53 AM
  #6  
tsigwing's Avatar
Senior Member
10 Year Member
Liked
Loved
Community Favorite
 
Joined: May 2015
Posts: 2,169
Likes: 640
From: Garland, Tx
Default

why does it work on the interior outlet, but not the bed outlets?
Reply
Old Sep 12, 2025 | 11:01 AM
  #7  
spammagnet's Avatar
Senior Member
5 Year Member
Photogenic
Liked
 
Joined: Nov 2016
Posts: 922
Likes: 308
Default

Originally Posted by Jim Fountain
Start up current too high. Dogbone will probably fix it. Try this:

https://www.amazon.com/WEN-PC1405-10...s%2C147&sr=8-5
That's an interesting workaround.
Reply